What problems do you have? If you have problems with connection "Can not connect to the server" message is appeared, ping your PLC. If you have "Connection Lost" message check settings of Allen Bradley do you have. Check Slots and other settings. Watch this video: teslascada.com/videotutorials/teslascada...or-allen-bradley-plc .
Best regards,
Ruslan
The administrator has disabled public write access.
Sto utilizzando una CPU CompactLogix L24ER, la cpu in slot_0 di default (non modificabile)
Impostazioni come da esempio
IP 192.168.0.99
port 44818
slot 0
backplane 1
messaggio di errore "connection lost"
è necessario qualche accorgimento in PLC?
mi può inviare esempio
The administrator has disabled public write access.
Connessione con CompactLogix Rockwell Automation
1 year 7 months ago #1179
Check your tag settings. Do you click "..." in Tag properties->PV Input tag to setup your Pointer settings? The message "Connection lost" means that you can connect to your PLC but can't get data. That means that you incorrect setup tag. After setting tag it should look like at the attached file. If you still has problem send me your project.