TOPIC: I Can't See Modbus Server TCP

I Can't See Modbus Server TCP 3 years 2 weeks ago #1327

  • Barone
  • Barone's Avatar
I talk to my modbus TCP server with different applications including modbusSIM, but I can't do it with TeslaScada2, Server IP same, Area HR same ..
but nothing ... Help
An example? ... thanks
The administrator has disabled public write access.

I Can't See Modbus Server TCP 3 years 2 weeks ago #1328

  • fatkhrus
  • fatkhrus's Avatar
  • Offline
  • Administrator
  • Posts: 826
  • Thank you received: 123
  • Karma: -107
Hello,
Did you try to connect to Modbus TCP server by using TeslaSCADA2 Runtime?
If yes, what message do you have? "Can not connect to the server" means you use wrong IP address and TeslaSCADA2 Runtime didn't "see" your server.
"Lost connection" means you use wrong registers or you have to check/uncheck "RTU over TCP".

Best regards,
Ruslan
The administrator has disabled public write access.

I Can't See Modbus Server TCP 3 years 2 weeks ago #1329

  • Barone
  • Barone's Avatar
I try with teslascada2 IDE on PC....ON PC is present Runtime?
The administrator has disabled public write access.

I Can't See Modbus Server TCP 3 years 2 weeks ago #1330

  • fatkhrus
  • fatkhrus's Avatar
  • Offline
  • Administrator
  • Posts: 826
  • Thank you received: 123
  • Karma: -107
Yes, it's available PC version of TeslaSCADA2 Runtime. It's in the same archive you've downloaded from our site.

Best regards,
Ruslan
The administrator has disabled public write access.