Alarm Popup. 11 months 2 weeks ago #3396

Dear Sir ,

When alarm is active after one popup in runtime scada.How can off this feature not open the popup ?

Best Regadrs
Chetan Kashyap
The administrator has disabled public write access.

Alarm Popup. 11 months 2 weeks ago #3397

  • fatkhrus
  • fatkhrus's Avatar
  • Offline
  • Administrator
  • Posts: 1027
  • Thank you received: 136
  • Karma: -102
Dear Chetan,

What do you mean? Do you mean how to disable alarm next popup window? It's not possible.
Popup alarm window will be appear if next alarm is happened.

Best regards,
Ruslan
The administrator has disabled public write access.

Alarm Popup. 11 months 2 weeks ago #3398

For your attach the alarm popup .How can disable this popup?

Regards
Chetan
Attachments:
Last Edit: 11 months 2 weeks ago by CHETAN@0707.
The administrator has disabled public write access.

Alarm Popup. 11 months 2 weeks ago #3399

  • fatkhrus
  • fatkhrus's Avatar
  • Offline
  • Administrator
  • Posts: 1027
  • Thank you received: 136
  • Karma: -102
If you want that some Alarm is not appeared make its priority in Tag settings greater then priority you setup in Project properties.

Best regards,
Ruslan