TOPIC: Communication problem - 1212C v4.2 (Siemens)
Communication problem - 1212C v4.2 (Siemens)
6 years 1 month ago #643
alvaro.montano.chiara
Perform communication tests with a CPU 1214C v2.0 all good ; then I try the same operation with a CPU 1212C v4.2 and it does not establish communication .
Please your collaboration
The administrator has disabled public write access.
Communication problem - 1212C v4.2 (Siemens)
6 years 1 month ago #644
You should make some settings in TIA Portal to have possibility to work with S7-1200 PLC v 4.0 and higher. To check checkbox "Permit Access with PUT/GET communication from remote partner (PLC, HMI, OPC..)" in Protection menu of General tab in PLC settings of S7-1200. See attached picture.