Welcome, Guest
Username: Password: Remember me

TOPIC: Communication problem - 1212C v4.2 (Siemens)

Communication problem - 1212C v4.2 (Siemens) 6 years 1 month ago #643

  • alvaro.montano.chiara
  • alvaro.montano.chiara's Avatar
Perform communication tests with a CPU 1214C v2.0 all good ;) ; then I try the same operation with a CPU 1212C v4.2 and it does not establish communication :huh: .
Please your collaboration
The administrator has disabled public write access.

Communication problem - 1212C v4.2 (Siemens) 6 years 1 month ago #644

  • fatkhrus
  • fatkhrus's Avatar
  • Offline
  • Administrator
  • Posts: 863
  • Thank you received: 126
  • Karma: -108
You should make some settings in TIA Portal to have possibility to work with S7-1200 PLC v 4.0 and higher. To check checkbox "Permit Access with PUT/GET communication from remote partner (PLC, HMI, OPC..)" in Protection menu of General tab in PLC settings of S7-1200. See attached picture.



Best regards,
Ruslan
Last Edit: 6 years 1 month ago by fatkhrus.
The administrator has disabled public write access.
Go to top