TOPIC: TeslaSCADA2 - Modbus Connection Lost but works

TeslaSCADA2 - Modbus Connection Lost but works 3 years 5 months ago #1425

  • arifcorp
  • arifcorp's Avatar
  • Offline
  • Senior Member
  • Posts: 46
  • Karma: -1
Hi Ruslan

I managed to establish Mosbus/TCP communication Modbus Master. However, each time i run the run time, it pop up connection lost. However, it works fine.

Please advise



Thanks

Thanks
The administrator has disabled public write access.

TeslaSCADA2 - Modbus Connection Lost but works 3 years 5 months ago #1426

  • fatkhrus
  • fatkhrus's Avatar
  • Offline
  • Administrator
  • Posts: 858
  • Thank you received: 126
  • Karma: -108
Hello,

Do you have correct information? If not maybe you've got RTU over TCP connection. In this case you have to check "RTU over TCP" in server settings.
Or you've got bad ethernet connection. Try to increase "Poll interval" from 1000 ms to 2000ms.

Best regards,
Ruslan
The administrator has disabled public write access.

TeslaSCADA2 - Modbus Connection Lost but works 3 years 5 months ago #1427

  • arifcorp
  • arifcorp's Avatar
  • Offline
  • Senior Member
  • Posts: 46
  • Karma: -1
Hi Ruslan

The issues was i used the slave id 0 value. Which is broadcast value. Once change the slave id t 1, the problem solved. Thanks