TOPIC: Connect TeslaScada IDE to M221 PLC siulator

Connect TeslaScada IDE to M221 PLC siulator 2 years 10 months ago #1675

  • miftahuda
  • miftahuda's Avatar
  • Offline
  • New Member
  • Posts: 12
  • Karma: 0
Hello tesla team,

Could TeslaScada IDE connected to M221 somachine simulator?
If i use address %M0 (memory bit 0) in M221 PLC (Schneider), how about addressing in TeslaScada IDE?

Tq
The administrator has disabled public write access.

Connect TeslaScada IDE to M221 PLC siulator 2 years 10 months ago #1676

  • fatkhrus
  • fatkhrus's Avatar
  • Offline
  • Administrator
  • Posts: 852
  • Thank you received: 126
  • Karma: -108
Hello,

No, TeslaSCADA IDE can not connect to the PLC. You have to use TeslaSCADA2 Runtime to connect to PLC.
How to setup your project to connect to Modbus TCP device use this video tutorial: teslascada.com/videotutorials/teslascada...lesson-2-quick-start

Best regards,
Ruslan
The administrator has disabled public write access.

Connect TeslaScada IDE to M221 PLC siulator 2 years 10 months ago #1677

  • miftahuda
  • miftahuda's Avatar
  • Offline
  • New Member
  • Posts: 12
  • Karma: 0
ok , i tried using teslascada runtime, can connect with m221 somachine simulator

'vei used addresses in m221 : %M0 , %M1 and %M2 (All memory bit).
What are the addressing in tesla scada id for %M0 , %M1 and %M2?
The administrator has disabled public write access.

Connect TeslaScada IDE to M221 PLC siulator 2 years 10 months ago #1678

  • miftahuda
  • miftahuda's Avatar
  • Offline
  • New Member
  • Posts: 12
  • Karma: 0
what is the TAG addressing for %M0, %M1, %M2 in TeslaScadaIDE

tq
The administrator has disabled public write access.

Connect TeslaScada IDE to M221 PLC siulator 2 years 10 months ago #1679

  • fatkhrus
  • fatkhrus's Avatar
  • Offline
  • Administrator
  • Posts: 852
  • Thank you received: 126
  • Karma: -108
For %M0 you have to setup like at the attached file.



Best regards,
Ruslan
The administrator has disabled public write access.

Connect TeslaScada IDE to M221 PLC siulator 2 years 10 months ago #1680

  • miftahuda
  • miftahuda's Avatar
  • Offline
  • New Member
  • Posts: 12
  • Karma: 0
ok, well done for %M0 Ruslan, tesla scada runtime've connected to somachine plc simulator
How about for %M1 and %M2 addressing?
Any restricted for trial purposed (no license? I saw when using holding coils for Bit : inactived for addresing?

tq
The administrator has disabled public write access.